- Chapel Hill, NC
- Retired Electrical Contractor
Wired my first car charging station. Box states 30 amps circuit
Here are the instructions. What would you do?
Wall station should be installed only by a licensed contractor, and/or a licensed electrician in accordance with all applicable state, local and national electrical codes and standards.
? Ensure that a dedicated circuit capable of supplying 30A at 208-240 VAC, is available
? Power feed must have a centrally grounded neutral in order for WattStation to function correctly.
? Wall receptacle must be a NEMA 6-50 outlet. A recommended 40A upstream circuit breaker. located either in a panelboard or load center. should be used . Distance between the wall power receptacle and WattStation mounting should be less than one (1) foot
? Wall power receptacle with a weatherproof locking cover is required
? Recommended mounting hardware for wood studs are 3/8" x 2" hex head lag bolts
? Recommended mounting hardware for concrete walls are 3/8" x 1-3/4" concrete hex screws or 3/8" x 1-7/8"
concrete anchors