 - Chapel Hill, NC
 - Retired Electrical Contractor
It is a type of receptacle. By the definition of the NEC I would call it a receptacleThat does not answer my question. Is the power connection for the vac system a receptacle?
That is my point. If it is a receptacle and if it is connected to a 15 or 20 branch circuit, the code requires it to be a grounding type receptacle.It is a type of receptacle. By the definition of the NEC I would call it a receptacle
It's not really internal, the wiring is in the walls of the house.Unless it is considered as an "internal" connection within the UL-listed Central Vac system rather than a receptacle.
From what I've seen, it's fed from the closest receptacle.If is it fed from the Vac controller rather than from a panel, its wiring may not be a branch circuit under the NEC in the first place.
With all due respect to Dennis, I don't think that example works here. You are talking about the inside of an enclosed device that is listed for use in that exact fashion, vs. a product that's wiring is completely exposed and run inside of the walls of a dwelling.I think that the example of the internal receptacle and plug-attached fan inside a built-in exhaust fan housing really is a good comparison.
Is that not a receptacle connected to a 15 or 20 amp branch circuit?
(B) To Be Grounded. Receptacles and cord connectors that have equipment grounding conductor contacts shall have those contacts connected to an equipment grounding conductor.
	"Two wire romex ok for new branch circuit?"
You do not look stupid! We all have vision problems with advancing age.If I would have read the title and not just the post I would not look stupid.
I don't see (B) as changing (A).And then the NEC turns right around and reverses that. ...
I don't see how it can be an inlet...you have to have an outlet as the supply. You connect a supply to an inlet.So address my other two possibilities.
As far as it being a receptacle under the NEC...not sure...that is why I asked if it was.
I reread the OP and don't see the word "new" anyplace in that post:?"Two wire romex ok for new branch circuit?"
I would not call it a receptical as far as NEC is conscerned. I would say it is part of a listed assembly. The directions show it being taped off of a branch circuit receptical and not a continuation of the branch circuit
I bet that outlet is not TR either---:lol:
I have hooked up many of them and don't see an issue with it as long as it is a listed product. Nothing else can get plugged into it and no equipment grounding conductor is needed for the vac.
Somehow I don't think this is where the op was going
Where in the code does it state that an equipment grounding conductor must be run with the circuit conductors? If I had a two wire romex cable (hot and neutral wire), is it allowable to use it as a branch circuit with non-grounding type receptacles? Thanks
This is the tread title.I reread the OP and don't see the word "new" anyplace in that post:?
It is in the title of the post
Who reads that, :slaphead: unless you are selecting which thread to read![]()