- Placerville, CA, USA
- Retired PV System Designer
That was the assumption that I started with. And I have not seen anything to change that, although I am far from an expert on the subject. Hence the search for answers to that question also in this thread.For arc flash studies, to compare differences in 50Hz transformers vs. 60Hz, you only have to compare the transformer impedances.
If the 50Hz xformer and the 60Hz xformer have the same impedance (assuming same voltage and KVA), then wouldn't the arc flashes be very close to the same?
There will be more energy stored in the magnetized core of the 50Hz transformer since the integrated flux will be higher at the same voltage, if that has any effect. But I am guessing that the majority of the incident energy will be fed through from the primary.