At no load?
Unbelievable!
To you, perhaps.
Please do not just draw any thing to scale to prove it .
Did you give due consider the implications of the time-derivative term in Faraday's Law shows that the flux in the core is
the integral with respect to time of the applied voltage with respect to 60Hz and 50Hz?
I suspect not. Here is the time integral shown graphically to demonstrate the difference between that for 60 Hz and that for 50Hz.
It is perfectly clear that the 50Hz voltage time integral is greater than that for 60Hz.
The flux is thus demonstrably greater for 50Hz than 60Hz. I'm sure you can see that.
Please do some calculations also to prove it, if you have that much expertise, as I requested many posts back.
I already did. For a 480V 60Hz transformer to operate at design flux it would need to be energised at 400V on a 50Hz supply. It's that simple.
Let me give you another example.
The Steinmetz equivalent circuit I gave you also works for induction motors.
Induction motors are sometimes driven from variable frequency inverters. The most common mode of operation is constant voltage to frequency ratio. Constant V/f control.
So if you drop the frequency of a 480V 60Hz motor to 50Hz you also reduce the voltage to 50/60 of 480V which is 400V.
This keeps the operation in the constant flux region and the motor can generate rated torque at any speed.
If the voltage wasn't reduced, the motor magnetic circuit would saturate.
Normally, we charge a grand a day (Sterling) when I provide training for customers.
I have happily given you all this information/education in a way that I thought might be helpful to you. I think one of the great merits of this forum is that we
can freely share knowledge.
Maybe, just maybe, it is time for you appreciate that rather that refuting it.