jott
- Richmond, VA, USA
Is operating breakers in switchgear considered working on live equipment and require the PPE indicated on the Arc Flash warning label?
This issue came up because there is a site that had 4000A switchgear with no labels, they were replaced in kind with new 4000A switchgear but an Arc Flash study was completed and labels were installed as required. Several of the main sections are dangerous. The operations personal received training that they must meet the level of PPE on the label to operate breakers, so they say they cannot operate any of the switchgear with a dangerous label. This switchgear does not have remote control, it is main tie main with PLC control but manually directed from controls above the main breaker. Is it correct that the operations personal cannot safely operate this equipment? Does opening and closing breakers in switchgear with the doors closed require the same PPE as having the doors open? I?m looking in 70E and OSHA but I can?t seem to find anything that says operating breakers requires a lower level of PPE, only that hazards must be evaluated, but I can?t find any guidance for when it would be appropriate to lower the PPE required. How do others interpret this?
Thanks much.
Thanks much.