mivey
I'll buy that as a contributing factor but not the whole reason.Seriously though my amp clamps are not good at measuring accurately at low levels even my true RMS one.
English only please.I think we are overthinking this.
Can't forget the phasors as they are the answer.Forget the phasor additions and the issue of how close is "about" right. The measurements were 1 and 2 amps, but exactly how accurate were those measurements? Can a clamp on ammeter really distinguish 0.9 amps from 1.1 amps, so that we can say with confidence that the actual current was, in fact, 1.0 amps and not 1.1? We don't know how the measurements were taken, nor with what instrument, and we don't know the degree to which the loads were balanced on the panel as a whole (i.e., we don't know phase angles).
I agree....
I'll buy the power factor and the reading inaccuracies combined but not the readings alone because the phasors are key factors, IMO.
Ha-ha :happyno:The word phasor is like the bat signal for Smart.![]()
For the record, my post wasn't anything close to technical. But also for the record, it's hard to explain how neutral current on a 120/208V system can be greater than either line load without going technical...Just want to point out it's happening again, this thread is going technical without waiting for the OP to jump back in.
Deductive reasoning.I have no idea how you can make that call with the info given.
Your meter has a 600.0 A scale and accurate to 2% of reading +/- 0.5 amps so would not be the meter to use for a current reading of an amp or so.My Fluke 336 which is true RMS will show 1 or 2 amps sitting on the table. Move it around an open panel and the reading will be bouncing all around.
I will agree it is hard to explain without some technicalities. But some explanations are maybe more complex than need be for a somewhat simple answer.For the record, my post wasn't anything close to technical. But also for the record, it's hard to explain how neutral current on a 120/208V system can be greater than either line load without going technical...
I think such an outcome quite unlikely.I think your supply 120/208V is tapped from 3 phase supply and not 120/240V single phase supply. As such, there is no wonder you get 3 amps in the neutral.
What else are we going to do if he won't come out and play with us?Just want to point out it's happening again, this thread is going technical without waiting for the OP to jump back in.
We can say that... and I believe you just didI will agree it is hard to explain without some technicalities. But some explanations are maybe more complex than need be for a somewhat simple answer.
How about if we just say since the two phases are not 180 degrees apart, they do not completely cancel each other in a multiwire circuit using only two phases and the neutral of a wye system like they do in a single phase system or in a delta system with one phase grounded at the mid point?
Still having trouble with the word 'about', it's OK I know engineers hate imprecision.![]()
I think the OP also needs to verify the voltage between the two phase wires in his MWBC just to confirm he has different phases.
Because the OP recognizes that the simple answer is not enough and a more technical answer is needed:But some explanations are maybe more complex than need be for a somewhat simple answer.
...I expected to see something less than 2 amps on the neutral but was surprised to see the full 3 amps.
I agree it is unusual for normal loading. Definitely not a "it is no wonder" thing. In fact, it is a "I wonder why" thing which is why the thread caught my interest.I think such an outcome quite unlikely.