Doesnt add up with code descriptions in 2011
Doesnt add up with code descriptions in 2011
210.12 of the 2014 Code will require all 15 and 20-amp 120-volt outlets and devices (such as switches) to be on arc-fault protection, and this would include the garbage disposal. Even if it's hard-wired there's still a switch (device). Also if it's cord and plug connected it would have to be GFCI since the outlet is within 6' of the sink. Just wondered if anyone had thoughts or good or bad experience on this one?
I do agree on the AFCI requirement, no problem understanding that part. It is clear on outlets and devices in the kitchen requiring AFCI
I do not completely agree on the GFCI just because it is within 6' of a sink.
In the 2011, that rule was in effect for any non kitchen sinks already.
By their description, it has nothing to do with under cabinet receptacles.
They even have a nice picture/diagram to show the area around the sink.
Here is the description:
(7) Sinks ? located in areas other than kitchens where receptacles
are installed within 1.8 m (6 ft) of the outside
edge of the sink
Recognizing that sinks in kitchens are not the only location
where a ground-fault shock hazard exists, this requirement
covers all other sinks in a dwelling. This requirement does
not limit the GFCI requirement to only receptacles serving
counter top surfaces; rather, it covers all 125-volt, 15- and
20-ampere receptacles that are
within 6 ft of any point along
the outside edge of the sink
Was anyone required to use GFCI on a disposal in a Bar sink for the 2011 code?
All IMHO