2-177 Log #525 NEC-P02
Final Action:
Accept in Principle
(210.52(F))
________________________________________________________________
Submitter:
Kelvin McDowell, Randolph Community College
Recommendation:
Revise text to read as follows:
210.52(F)
Laundry
Areas.
In dwelling units, at least one receptacle outlet
shall be installed for the laundry equipment.
Substantiation:
By adding the word ?equipment? there would be no
misunderstanding that this receptacle is for the laundry equipment instead of a
receptacle to be installed for no reason or purpose. It seems to be the consensus
of electricians that this receptacle and the circuit required in 210.11(C)(2) does
not have to supply anything and the laundry equipment such as washing
machines, gas dryers, and smoothing irons installed in the laundry areas can be
supplied from a general purpose circuit.
Note:
Supporting material is available for review at NFPA Headquarters.
Panel Meeting Action: Accept in Principle
Revise
the proposed language as follows:
?210.52(F)
Laundry
Areas.
In dwelling units, at least one receptacle outlet
shall be installed in areas designated for the installation of laundry equipment.?
Panel Statement:
This revision clarifies the intent of this provision and
accomplishes the objective of the submitter.
Number Eligible to Vote: 11
Ballot Results:
Affirmative: 11