If I replace a breaker panel in a house built in 2001, do I have to use arc fault breakers?
I figure I do, but I just want to verify.
Couple of points first.
I believe that 'we' are still under the 2011 NEC. I cannot see anything on the BBS website that says we changed Jan 1st. I will know for sure tomorrow night.
Even that you have no inspections you are still required to follow the
RCO* so I am using the 2011 NEC.
210.12
(B) Branch Circuit Extensions or
Modifications ? Dwelling
Units. In any of the areas specified in 210.12(A), where
branch-circuit wiring is modified, replaced, or extended, the
branch circuit shall be protected by one of the following:
(1) A listed combination-type AFCI located at the origin of
the branch circuit
(2) A listed outlet branch-circuit type AFCI located at the
first receptacle outlet of the existing branch circuit
Discuss this with your attorney since I am not allowed to practice law in Ohio:
313.1.1 Alterations, repairs and additions.
When interior alterations, repairs or additions
requiring a permit occur, or when one or more sleeping rooms are added or created in existing dwellings, the individual dwelling unit shall be provided with smoke alarms located as required for new dwellings; the smoke alarms shall be interconnected and hard wired.
You have no permits required where you are but should you install these????? See comment above?
Yes to the AFCI's. Highly recommend the smokes.
* Opinion of Billy Phillips BBS on 2 Jun 2006 at the first class on the RCO. Question asked by yours truly.