Hi, i just failed my temp / permanent meter base inspection for lack of UFER. The install is in a remodeled house, with existing basement (where panel box is located). I installed two new ground rods min. 6 ft apart as well as a #6 awg to the buried cold water line 12" from entrance. The inspector has failed me for lack of UFER and certification, CEE with existing footing/slab? I have read the NEC code over and over, and from what i see as long as i have two ground rods plus cold water ground i should be good. Let me know if i am wrong.