Combo inspector was not in Ohio.
Combo inspector was not in Ohio.
As an update,
I finally worked it out with the county inspector, the plumbers had cut open the concrete slab to run the groundwork, so i ended up installing 20'+ of rebar in the open pit, and stubbed up about 6" of the rebar and grounded it to the panels.
Thank you for everyone's response!
-HDT
The building inspector does this for our town and if a copper extension is installed the concrete contractor installs it. The copper part should go away when we adopt the 2014 in June as that specifically permits a rebar extension out of the concrete for the connection of the GEC.I hope that inspector has an ESI or he has a major problem(Ohio). Building Inspector can't do that.
If the BBS allows this I'd like to see that opinion.
The problem with that is that in many cases no electrical contractor has the contract at the time of the pour. That is why this inspection is done by our building inspector and why the concrete contractor has to supply an external connection point for the GEC.I think that's where the certification part comes in.
I believe its the EC's responsibility to be there after rebar is installed then get it inspected prior to concrete pour. In most jurisdictions I have been involved with, a structural pre-pour inspection is required, too, and both inspections are often performed by the same inspector.
The NEC requires the rebar to be in a footing, not a slab to create a UFER.As an update,
I finally worked it out with the county inspector, the plumbers had cut open the concrete slab to run the groundwork, so i ended up installing 20'+ of rebar in the open pit, and stubbed up about 6" of the rebar and grounded it to the panels.
Thank you for everyone's response!
-HDT
Kind of hard for the EC to be there before the pour if no EC has been secured .The problem with that is that in many cases no electrical contractor has the contract at the time of the pour. That is why this inspection is done by our building inspector and why the concrete contractor has to supply an external connection point for the GEC.
The NEC requires the rebar to be in a footing, not a slab to create a UFER.
Tapatalk!
...
I finally worked it out with the county inspector, the plumbers had cut open the concrete slab to run the groundwork, so i ended up installing 20'+ of rebar in the open pit, and stubbed up about 6" of the rebar and grounded it to the panels.
...
That's not an approved electrode...
The NEC requires the rebar to be in a footing, not a slab to create a UFER.
I believe he was referring to the remedy not being in foundation or footing.FUBAR # 2 slab should have vapor barrier and not in direct contact with earth