Where is the code does it address when this type of cable does and does not have to be installed in a raceway?
Article 760, for both power limited and non-power limited fire alarm circuits. Wiring for Class 2 and Class 3 circuits can share the same raceway/wire loom/J-hook. Metallic or non-metalic raceways and article 300 wiring methods are generally not required, except where specified in 760. Of course, local requirements and job specifications may be more restrictive. We do work in a power plant and everything goes in 3/4" RMC at a minimum.