This is a wo part question--I thought I understood article 300.3 but I am having a bit of an issue with it. Here is the first paragraph
Now does this mean if a grounded conductor is used in the circuit then it must be run with the circuit conductors? What I am getting at here is why are we allowed to run a switch loop down from a light with the feed in the ceiling-- thinking pipe here for the time being. It would appear by doing this electromagnetic field's are created except that the metal conduit would contain it but it still seems to violate 300.3(B). Input please
I know I never looked at it that way before but I have a job that has a issue with electromagnetic field's in a residence because the switch leg was run from a 4 way switch instead of fed at one end and switch legged out the other. This job is nm cable and I get high readings at the 4 way but not at the 3 ways.
Situation is 3 way feed- 4way in the middle other 3 way dead end-- switch leg in the 4 way. I realize the electromagnetic field is created because the neutral is run apart from the switch loop but why is it only showing at the 4 way?
(B) Conductors of the Same Circuit. All conductors of the same circuit and, where used, the grounded conductor and all equipment grounding conductors and bonding conductors shall be contained within the same raceway, auxiliary gutter, cable tray, cablebus assembly, trench, cable, or
cord, unless otherwise permitted in accordance with 300.3(B)(1) through (B)(4).
Now does this mean if a grounded conductor is used in the circuit then it must be run with the circuit conductors? What I am getting at here is why are we allowed to run a switch loop down from a light with the feed in the ceiling-- thinking pipe here for the time being. It would appear by doing this electromagnetic field's are created except that the metal conduit would contain it but it still seems to violate 300.3(B). Input please
I know I never looked at it that way before but I have a job that has a issue with electromagnetic field's in a residence because the switch leg was run from a 4 way switch instead of fed at one end and switch legged out the other. This job is nm cable and I get high readings at the 4 way but not at the 3 ways.
Situation is 3 way feed- 4way in the middle other 3 way dead end-- switch leg in the 4 way. I realize the electromagnetic field is created because the neutral is run apart from the switch loop but why is it only showing at the 4 way?