GScollins
- Drumright, Oklahoma
I am having trouble figuring out what permits, etc., are required for certain tasks. Our safety person thinks that I need to call out utility company and shut off all power coming into the boxes since there are still hot wires in the top of the box.
Example 1 would be terminating new branch circuit conductors on breakers in a main breaker panel with the main breaker turned off and bolted covers removed. Is this example going to require a energized work permit?
Example 2 would be terminating the same new branch circuit conductors to breakers(off) with main breaker on and buss exposed with bolted covers removed and some other breakers turned on.
Neither example would be working on energized parts, but would be near energized parts.
Example 3 would be changing fuses or landing load wires in a 100 amp 480 volt disconnect with line side still energized, disconnect off, arc shields still in place
I assume all 3 would require wearing proper level of arc flash suit. But I get confused about LOTO and energized electrical work permits.
Does any of this make sense? And how do you approach this?
thanks
thanks