Anybody know, in general, how close these codes compare?
Anybody know, in general, how close these codes compare?
There is an ongoing process to bring the two codes closer together. The changes in the ampacity tables for the 2011 NEC was part of that process.
Canadian 125V 20A receptacle only allows a 125V 20A plug.
While I'm no Canadian code expert, my understanding is that only applies to service conductors.I think they don't allow feeder conductors and branch circuit conductors in the same enclosure without a barrier. That is why they mount residential panels sideways, I hear.
While I'm no Canadian code expert, my understanding is that only applies to service conductors.
In the NEC, it only applies to mixing service (without OCPD) conductors with feeder or branch (after OCPD) conductors.
If Canada is different on this, then it would have to affect a non-service conductor situation.
Not only are the service conductors isolated from the rest of the panel, so is the main breaker. With the type of service panels required by the CEC, you can turn off the main breaker and work in the panel without violating the electrical safe work rules...something that can't be done the way we install service equipment. If we want to comply with the OSHA rules and the rules in 70E, and work in a panel that contains the service disconnect, we have to have the power upstream from the panel turned off. Something that, in most cases, requires action by the utility and something that is almost never done for residential or commercial work....
And no, I'm told this relates to service conductors entering a panelboard and they have to be isolated from other conductors within the panel. If the panel is fed by a feeder this does not apply.
...
But what about kitchen T slot GFCIs? Or is that a recent allowance?
In the NEC, it only applies to mixing service (without OCPD) conductors with feeder or branch (after OCPD) conductors.
If Canada is different on this, then it would have to affect a non-service conductor situation.
But what about kitchen T slot GFCIs? Or is that a recent allowance?