You can't (easily) feed it with anything other than 14ga wire, so 15A is fine. The motor overload protection is supposed to protect the motor for actual running load amps, if the motor has no overload protection built-in, then you will need an external OL relay.Hi all.
To feed a 2.5 hp motor (I will have to look at the chart for amperage but)
The motor reads 4.5 amps at 220v
At 250% is max oc protection of 11.25 amps.
Does the next size higher at 15 amp apply to this or do I have to protect it at 10.
Thank you
Thank you. Yes it's tp.
Reading about its short circuit ground fault protection at the 250% it says no more than.
It doesn't say anything about an exemption.
Are you sure the first two are not 3 phase motors? Those values are WAY low for that voltage class single phase motors. There are always differences in efficiency that show up as differences in FLC, but that is way beyond that. Those first two values are down in the 1/2HP range for single phase motors... Maybe it's not "2-1/2HP" as in "2.5HP" but rather "2 x 1/2HP".Thank you. Yes it's tp.
Dang pools. :- )
3 motors.
A 1.5 hp that reads at 220v is 4.5
1.1 hp that reads at 230v is 5.1
1.65 hp that reads at 230v is 10
The 1.65 actually reads 1.5 hp sf 1.1 total hp 1.65
Why such a large difference between the two 1.5 hp motors?
So instead of using two 15 amp gfci breakers
And a 20 amp gfci breaker ( 3 total)
I'm hoping to use 1-15 amp or 20 for the two. And one 20 amp for the largest ( 2 total)
But even if one breaker per motor is the 15 too large?
Are you sure the first two are not 3 phase motors? Those values are WAY low for that voltage class single phase motors. There are always differences in efficiency that show up as differences in FLC, but that is way beyond that. Those first two values are down in the 1/2HP range for single phase motors... .
It's probably one of those marketing issues with regard to "HP". They can get away with it because they are really only REQUIRED to list the amps and volts, HP is not strictly defined so it's something that can be interpreted. So in the retail business they often use the concept of "develops" a certain HP as their interpretation. What that means is that under Break Down Torque conditions, the PEAK torque, which is 200-220% of Full Load Torque, when factored into the slip speed it takes to get there, can be expressed as a "developed" HP capability, however momentary that can be maintained. It's total BS and would NEVER fly in the industrial world, but there is nothing saying they can't say it, so they do, knowing that the vast majority of retail consumers will have no clue.LOL
What's up with that? I see too.
From a protective device standpoint, you use the nameplate amperes info and 430.52 (or 53) rules. From a conductor sizing standpoint, you must use the HP ratings... but in this case you are going to end up at 14ga for each individual motor anyway.OK.
So now do I rate the circuit for the HP or the amperage?
LOL