sfav8r
- San Francisco Bay Area
We had the following items called on an inspection. I really don't understand the calls, maybe someone can elucidate me. All we did was upgrade the panel. No work was done in the home. SFD with 200a service.
1) #12 wire is being fed with 15a circuit breaker. Replace circuit breaker .
2) There is a #12 wire in the panel that is spliced to a #14 wire in the junction box in the garage. Remove #12 wire and replace with #14 wire. (FYI, this was on a 15a breaker)
3) Gas pipe is only bonded where it enters the home. Add gas pipe bonding at HW heater.
4) There is only 1 15a lighting circuit. Two 15a lighting circuits are required.
5) Confirm name plate rating on electric stove. Current 30a circuit may not be sufficient.
#1,2 So, for my thinking, #1 makes no sense to me at all. #2 I understand his point but I do not believe this is an NEC issue.
#3 What? It is bonded as required and we need another one at the HW heater?
#4 what code is this?
#5 What the heck, now we have to run a new circuit from the panel to the upstairs kitchen for a stove that has been there for 8 years?