This has been brought up before and David seems to think those are exceptions and do not add to the conversation. :huh::?
I thought so, but I didn't reread the whole thread to verify.
Mentioned sections would allow feeders with different supply characteristics.
There is similar wording in art 230 for services with different supply characteristics.
Nowhere does NEC specifically address supply being from both feeders and services. ADD: maybe I should say nowhere does it limit supply to be from feeder or service only but not both.
But to have a service and a standby generator (which is going to be either feeder or branch circuit, but not a service) is common, so something is assumed somewhere I guess for that application. And it goes beyond the either you are supplied by service or the generator, if that were the case then "whole house" transfer would be the rule, but you can have a generator that backs up only selected loads, and in such case you can supply those loads from the generator while everything else is simultaneously powered by the service.
I agree with this.
I enjoyed the lively discussion in this thread and found it to be very thought provoking but I too don't have anything new to add that hasn't already been said, so I will stand down.