It may not happen here, buy it is my hope that we end up at a common point. Hopefully, that the service has to be sized to handle the calculated load.
Since the service already has to be sized to handle the loads associated with the building it would be pointless to add an additional supply unless we move into one of the exceptions in articles 230 and 225 or special provisions found in other sections of the NEC.
I also think it is a more reasonable approach that article 225 is laid out, that the service(S) (one of each type allowed) is supplied to the premise under single management, and from the load side of the service (S) disconnect location additional buildings and structures are supplied by a single feeders or branch circuit..
Since the service already has to be sized to handle the loads associated with the building it would be pointless to add an additional supply unless we move into one of the exceptions in articles 230 and 225 or special provisions found in other sections of the NEC.
I also think it is a more reasonable approach that article 225 is laid out, that the service(S) (one of each type allowed) is supplied to the premise under single management, and from the load side of the service (S) disconnect location additional buildings and structures are supplied by a single feeders or branch circuit..