70E 2015 changes
70E 2015 changes
An advanced issue of the changes being adopted for 70E 2015 shows an addition to section 130.2(A) Energized work. Currently it's: 130.2(A)1 when greater hazard exists if not addressed, (A)2 Infeasibility (e.g. troubleshooting), (A) 3Less than 50 Volts, and now (A)4 Normal Operation, stating that normal operation of electric equipment shall be permitted where 5 conditions are met: 1-installed properly, 2-maintained, 3-doors closed and secured, 4-covers in place, 5-no evidence of impending failure.
I think this is acknowledgement that the risk is low. What I can't tell from what was published (EC magazine, Change is on the way! 2015 NFPA 70E) is the PPE requirement. I think this means that disconnect switches can be operated without PPE.
This stance is taken by Square D Data Bulletin 0100DB0804R11/09, PPE Recommendations, which lists four types of Square D gear: Power Zone II, 4, QED-6, QED-2, that shows "normal" switching is PPE 0, with similar stipulations, including commissioning and under load for some time.
This would make much more sense for the industry as a whole, to be able to operate a disconnect switch without PPE.
But then what if there are 100 calories available at the switch...??.. Perhaps the facility's Electrical Safety Program excludes those conditions.
Opinions welcomed!