Ok I'm going to try this one more time. 250.32 (A): "Buildings or structures supplied"... note there is no use of the term "attached" here, it merely says supplied. Note also: "shall have a grounding electrode or grounding electrode system installed [in accordance with article 250]." "Shall be connected in accordance with 250.32 (B) or (C). "Where there is no existing grounding electrode [or system], the grounding electrodes (s) shall be installed." (It actually uses the word installed twice.)
Although at earth potential, whether steel-walled or concrete, the equipotential grid is not an electrically connected grounding electrode system. We have to install one, the single exception being the single branch circuit. Very few inground swimming pools, btw, are supplied by a single branch circuit. Most have at least one light and a pump/filter. The shaft of that pump is inserted into the water jacket at the pump. That steel shaft is electrically connected to the pool through the water. We can't say this circuit for the pump does not supply the pool. It's every bit as electrically connected as the light is.
Am I going to install a ground rod for a subpanel in the typical residential installation? Hell no. I'm just pointing out that y'all are wrong.
And again, although the pool may be defined as a structure, it is not what is being supplied by the feed or branch circuit. Supplied meaning supplying power to the whole structure for distribution as needed. The equipment for the pool is what is being supplied. As has been said, if the panel for the pool equipment is at a separate building or structure than where it is being fed from, then a GES is required there. Obviously the panel/service it's fed from will have a GES also.
Since 250.32 says the GECs shall be installed according to 250.32(B) (for a grounded system), let's look at what 250.32(B) says:
(B) Grounded Systems.
(1) Supplied by a Feeder or Branch Circuit. An equipment
grounding conductor, as described in 250.118, shall be
run with the supply conductors and be connected to the
building or structure disconnecting means and to the grounding
electrode(s). The equipment grounding conductor shall
be used for grounding or bonding of equipment, structures,
or frames required to be grounded or bonded. The equipment
grounding conductor shall be sized in accordance with
250.122. Any installed grounded conductor shall not be connected
to the equipment grounding conductor or to the
grounding electrode(s).
Look at the part in red. Does the pool (defined as structure) have a disconnecting means?
No it does not, the structure where the panel is does, but not the pool it's self.
So the pool it's self is not what is receiving the feeder or branch circuit for distribution.
Before you say that a light or chair lift, etc. is a branch circuit, they are but not a branch circuit that is supplying the entire pool/structure for distribution.
If you build a barn or shed and put a panel in there, obviously it needs a GES. Now out of that barn you run (8) branch circuits outside for receptacles, lights, etc., would you go drive a ground rod at each circuit? What if these receptacles were mounted on wooden poles, would you have to drive a ground rod at each pole?
I don't think so!:happyno: