But are you feeding the pool with a service or feeder, or are you supplying the pool with branch circuits originating at a "separate structure"?Again I think you're all obfuscating all over the place here: 250.32 (A) specifies a grounding electrode or grounding electrode system, except in the case of a single branch circuit. 250.32 (A) states that the grounding electrode conductors shall be in stalled in accordance with 250.32 (B) or (C).
I'm saying a pool is a "structure"; it requires a grounding electrode or grounding electrode system AT the structure, which must be wired in accordance with 250.32 (B).
End of story.
Not really because I have no intention of installing the ground rod either. In fact I find it a little redundant even in the case of an actual structure. My point is that we've been playing these games since the 60s and it's time we focused on getting it - the NEC - right.
A ground rod is never required anywhere by NEC - it is just the most common electrode of choice when not others are available. An in ground pool will by design have a concrete encased electrode present. Equipotential bonding rules only require to tie things together with at least 8AWG. Depending on the service or feeder you may need larger then that for the GEC connection to it. But again the service or feeder is never at the pool it is at a nearby separate structure.