And again, although the pool may be defined as a structure, it is not what is being supplied by the feed or branch circuit. Supplied meaning supplying power to the whole structure for distribution as needed. The equipment for the pool is what is being supplied. As has been said, if the panel for the pool equipment is at a separate building or structure than where it is being fed from, then a GES is required there. Obviously the panel/service it's fed from will have a GES also.
Since 250.32 says the GECs shall be installed according to 250.32(B) (for a grounded system), let's look at what 250.32(B) says:
Look at the part in red. Does the pool (defined as structure) have a disconnecting means?
No it does not, the structure where the panel is does, but not the pool it's self.
So the pool it's self is not what is receiving the feeder or branch circuit for distribution.
Before you say that a light or chair lift, etc. is a branch circuit, they are but not a branch circuit that is supplying the entire pool/structure for distribution.
If you build a barn or shed and put a panel in there, obviously it needs a GES. Now out of that barn you run (8) branch circuits outside for receptacles, lights, etc., would you go drive a ground rod at each circuit? What if these receptacles were mounted on wooden poles, would you have to drive a ground rod at each pole?
I don't think so!:happyno: