Quote Originally Posted by transman2 View Post
I believe maybe a ground plate or something could be put in place so when the containers are set on the ground they will be grounded into the system which will trip the up steam breaker if same thing happens. If someone has seen a better way please let me know and does the code require this. Your thought! Thanks!
Quote Originally Posted by transman2 View Post
However the reefer container sit 2' away and don't touch in any way. The reefer container has a male plug on SOW cord that connects to the outlet mounted on the structure. The container relies on the EGC in the cord to wired correctly. Therefore if the ungrounded conductor and the EGC in the cord are swapped the container can become energized. I hope this helps.
Quote Originally Posted by GoldDigger View Post
OK, the best thing to do for safety, including avoiding dangerous situations caused by miswired cords on the units, is to provide a separate ground/EGC wire which is connected to each unit totally separately from the cord and outlet. It needs to be attached before you plug in the cord.
The only other way I can see to get protection is to install a ground fault circuit interrupter protecting each receptacle/outlet. For a 480V system, that may take some searching.
But do not just do nothing, as 480V can be extremely dangerous, as you have discovered.
Ground fault waring comes to mind,
Testing
Assured Equipment Grounding Conductor Program.
(1) All equipment grounding conductors shall be tested for continuity and shall be electrically continuous.
(2) Each receptacle and attachment plug shall be tested for correct attachment of the equipment grounding conductor. The equipment grounding conductor shall be connected to its proper terminal.
(3) All required tests shall be performed as follows:
a. Before first use on site
b. When there is evidence of damage
c. Before equipment is returned to service following any repairs
d. At intervals not exceeding 3 months
and i like your idea of a bonded steal plate to set the containers on
Reply With Quote Reply With Quote Multi-Quote This Message .
--------------------------------------------------------------------------------
Yes, the upstream 400 amp branch bkr is GFCI and will take all your comments to my next meeting. I hope most of you are in agreement that I can reference 250.32 and 250.50 to support additional grounding, preferably a grounding pad of some sort that's tied into the grounding system. I will also ask that additional testing on plug and cord before plugging in as well. Thanks for all your comments and hopefully we can make this a safer place to work.
Thanks!!!!