transman2
- Brooklet,Ga.
I hope I get lots of feed back on this question. At a Container Port I have found what I believe is a serious situation where, just picture a 4 story reefer rack that can accommodate 12 reefers plugging in at 12 outlets. Its a 3 phase 480y system. A worker got injured because the ungrounded conductor and the EGC were swapped accidently in the plug/cord that's attached to the container reefer. The container became energized and the worker went phase to ground when touching two containers. The outlet at the rack has a 32A breaker and there is a 400A upstream branch breaker that feeds 12 outlets at each rack. I believe the Container can be classified as a structure, and 250.32 and 250.50 should apply. I believe maybe a ground plate or something could be put in place so when the containers are set on the ground they will be grounded into the system which will trip the up steam breaker if same thing happens. If someone has seen a better way please let me know and does the code require this. Your thought! Thanks!