MJ1963
- new york, ny
I've worked with power meters that have typically 3 cts on each of the phases. When would a CT on the neutral bus be needed? Could someone clarify?
Thanks.
Thanks.
What I can't figure out is how a 2-element meter can properly measure 120/208Y 4-wire service. How do you zero-sum 4 wires with only 2 CTs?
Mathematically, there is never a need for a CT on the neutral for metering, since the neutral current must be the vector sum of the line currents.
The only thing a neutral CT in addition would be needed for would be for detection of a ground fault.
What exactly is being metered? Many replies are assuming this is for a POCO Watthour meter, if that is not the case or there is more ability then just measuring energy consumed, there may be good reason, ability to measure neutral harmonics was also a suggestion.I've worked with power meters that have typically 3 cts on each of the phases. When would a CT on the neutral bus be needed? Could someone clarify?
Thanks.
I found this diagram showing a 2 element Form 5S meter on 4-wire 120/208Y. Maybe that's what I saw? (I watched them swap in a smart meter at one of our facilities and I swear they only connected two CTs)You're right. A two element 3 phase meter (Form 5S) is for 3W Delta only. It uses two CT's and two Voltage inputs plus neutral. To measure 3 phase 4 Wire WYE, you need at least a 2 1/2 element meter (Form 6S). That uses three CT's and two Voltages plus neutral. It assumes the third voltage is the same as the average of the other two. Old technology, though. It was used to save the cost of one Voltage transformer. Now we use 3 element meters (Form 9S) for 3 phase 4W Wye and (Form 8S) for 3 phase 4W delta. Search for "Kwh meter Form diagrams" if you want to see how they're wired.
AHA! Yes, note that the middle line is wired in series through both of the other CTs. That will only work to the extent that the load is balanced. It avoids having to incorporate a sqrt(3) calibration factor into the meter, and it will still give an approximately correct answer with a small level of imbalance. But IMHO it has to be incorrect for different cases of loads on one of the phase lines or phases only.I found this diagram showing a 2 element Form 5S meter on 4-wire 120/208Y. Maybe that's what I saw? (I watched them swap in a smart meter at one of our facilities and I swear they only connected two CTs)
Just as the normal 120/240 3-wire meter assumes that the two line to load voltages are equal, this setup makes assumptions about the loads themselves.
In particular, this circuit apparently assumes that the loads are either delta or balanced, so my earlier qualification about two CTs being sufficient for delta wiring takes effect. If you tried to do the same thing with a wye system, you would lose big.
Yes, I meant line to neutral voltages.[Just as the normal 120/240 3-wire meter assumes that the two line to load voltages are equal, this setup makes assumptions about the loads themselves.]
GoldDigger, "line to load voltages"? Not sure what you mean by this? A Form 2S (standard 240 3W 200A) residential meter is 240V and does not require line to neutral voltages (if that's what you meant) to be balanced in order to meter accurately. The two line to neutral voltages always add up to line to line, regardless of imbalance. The voltage coil is line to line across the top jaws. The two current coils are just aluminum bus bars top jaws to bottom jaws. Don't want to hijack this thread, though. Just curious.
The problem is that the common meter measures both line currents and assumes that each current corresponds to one half of the line to line voltage. The neutral does not even connect to the meter.
Imagine that there is a severe voltage drop problem in the service wires.
With a one sided load the line voltages at the meter might be 110 and 120.
The meter would calculate as if the power delivered was at 115 volts instead of 110 volts. The error is small, but it will always be in favor of POCO.
If the voltage imbalance at the meter is inherent in the distribution and not related at all to local load, the error can favor either POCO or customer, but will statistically average out to zero over the customer base.
One thing to think about is that residential meters measure KWh. Utilities supply KVAh. Any power factor less that unity results in more current being supplied than what is measured. Probably makes up more than the difference. In your example, if you have a service that's 120V @ 30A and 110V @ 50A, (for an hour) the meter would register 9.2 KWh only if PF was unity. Actual would be 3.6 KVAh + 5.5 KVAh = 9.1KVAh. But at a .989 PF, the measured value would also be 9.1 KWh. Actual PF is probably lower than that on most services. But, too early in the morning to think about this stuff. Gotta go get another cup of coffee.![]()
One thing to think about is that residential meters measure KWh. Utilities supply KVAh. Any power factor less that unity results in more current being supplied than what is measured. Probably makes up more than the difference. In your example, if you have a service that's 120V @ 30A and 110V @ 50A, (for an hour) the meter would not register 9.2 KWh only if PF was unity. Actual would be 3.6 KVAh + 5.5KVAh = 9.1KVAh. But at a .989 PF, the KWh would be 9.1 KWH. Actual PF is probably lower than that on most services. But, too early in the morning to think about this stuff. Gotta go get another cup of coffee.![]()
The CT in the meter, or the current coil in a series connected meter, will always detect current, but they will include the timing information as well, so that the meter can record the vector product of that with the voltage.
Industrial meters also do this for the proportional part of the bill. The difference is that they also record the maximum PF (or the maximum KVA) for separate use in assessing a non-proportional penalty or fee as part of the monthly bill.