Well we can't have anarchy can we?There are, IMO, no situations which will systematically favor the customer.![]()
For pure resistance the angle would be 180 deg, but VA has a power factor angle associated with it so it is not correct to sum VA values. To sum VA directly you must use the power factor angle and make a vector addition.Why? VA does not take into account phase angle between voltage and current, so I though for single phase, it was VA = V x A and Watts = V x A x PF. Not so? Residential metering is Line to Line, so wouldn't angle between each leg be 180 deg? Been a LONG time since I had to remember this stuff. Makes my head hurt! Not too old to learn, though.
You can prove that for an n-wire system, you can use n-1 stators as long as the voltages all tie to a common wire without the CT (Blondel's Theorem).I think a simpler way of looking at why you don't need to monitor the neutral with a CT.
is that any current that flows through the neutral has to has to flow in either line #1 or
line #2 and has already been added.
For Three phase using Two CTs. instead of Three, the same might be true because any current that has to flow through the phase leg without the CT. has to flow through one of the other two phase legs with CTs.
But this might be debatable.
We can break the VA into W and var components (i.e. the rectangular components of the apparent power) and sum them separately. We can then use the resultant W and var totals to get the resultant VA.
In your example Wh and VAh had the same value but we accumulate Wh and varh, not VAh.
Weights and measures authorities must have decided the design was fair enough, and they generally lean toward favoring the customer and not the seller of a product or service if there is going to be any error in measurement.I do not have any reason to suspect that the less expensive meter was designed to give POCO an edge.
But if it gave the customer an edge POCO might have been less likely to settle for that design.