Mechanical meters make use of induced currents in the aluminum disk to provide a force on the disk which is proportional to the product of the instantaneous current and the instantaneous voltage. With the resistance supplied proportional to the speed of the disk, you now have the disk rotating at a speed proportional to the kW, not the kVA.
and without any additional mechanical devices in the dial chain, the disk will rotate backwards during reverse power flow (such as from local generation.)
And what the utility sells is energy produced by its generators, and a higher kVA delivered to the customer does not cost more fuel. It just requires larger distribution lines.
True....watts are what does work, but power is bought and sold based on both MWh and MVARh (added costs when PF is below specified values). That helps offset the construction and equipment costs associated with higher than optimal currents due to low PF. All of our equipment is sized by KVA rating, not KW. Somebody has to pay for the larger wire, transformers, etc. when PF will be less than unity. Those costs are ultimately passed on to the consumer. If billing was based on KVA, the worse the PF, the more you'd pay. That's how utilities have to buy their power. It's an incentive to keep PF under control. Saves money on infrastructure during construction and power costs for purchasers (like us) later. Generation fuel costs are only part of the overall pricing. Adding capacitor banks, static VAR systems, etc. isn't free. Ain't this stuff fun? Bet we've either lost or bored almost everybody. Including me. I think we've killed this dead horse. Bye.