If I supply a refrigerator with an IBC are you saying that it is not a small appliance branch circuit?
That is exactly what I have been saying.
Because if you are then art. 210.52(B) (1) would disagree with you, IMO
How so?
If I supply a refrigerator with an IBC are you saying that it is not a small appliance branch circuit?
Because if you are then art. 210.52(B) (1) would disagree with you, IMO
That is exactly what I have been saying.
How so?
It states that the small appliance branch circuit shall serve all counter, floor , wall etc and refrigerator equipment
Yes it does.
Then the exception changes that and tells us we can supply the outlet for refrigeration from an IBC.
That is what exceptions do, they change the main rule.
To me this is very clear and straight forward.
If I supply a refrigerator with an IBC are you saying that it is not a small appliance branch circuit? Because if you are then art. 210.52(B) (1) would disagree with you, IMO
(B) Small Appliances.
(1) Receptacle Outlets Served. In the kitchen, pantry,
breakfast room, dining room, or similar area of a dwelling
unit, the two or more 20-ampere small-appliance branch
circuits required by 210.11(C)(1) shall serve all wall and
floor receptacle outlets covered by 210.52(A), all countertop
outlets covered by 210.52(C), and receptacle outlets for
refrigeration equipment.
Exception No. 1: In addition to the required receptacles
specified by 210.52, switched receptacles supplied from a
general-purpose branch circuit as defined in 210.70(A)(1),
Exception No. 1, shall be permitted.
Exception No. 2: The receptacle outlet for refrigeration
equipment shall be permitted to be supplied from an individual
branch circuit rated 15 amperes or greater.
Here it is
Exception No. 2: The receptacle outlet for refrigeration
equipment shall be permitted to be supplied from an individual
branch circuit rated 15 amperes or greater.
By context, the exception permits an SABC for a refrigerator to be supplied by IBC (15A or greater). The exception does not say the circuit is non-SABC.Here it is
By context, the exception permits an SABC for a refrigerator to be supplied by IBC (15A or greater). The exception does not say the circuit is non-SABC.
If I supply my refrigerator with a 20 amp individual branch circuit and the Rec is placed at counter height just over the counter next to the refrigerator, can I supply the rest of the counter Rec with just one additional 20 amp counter circuit?
That wasn?t David?s point. He was suggesting that the countertop receptacle that happens to be a simplex and that happens to have a fridge plugged into it could count as one of the two required SABCs, so that only one more would be needed. I am inclined to agree, though I suspect most of us would consider that a poor design.I fail to see it being an "individual branch circuit" if it supplies the refrigerator and a countertop receptacle.
We don?t have to know or care what the homeowner chooses to plug into any given receptacle. If it is above the countertop, and if it is on a 20 amp circuit (individual or otherwise) then it is a SABC.If it is a simplex receptacle dedicated to the refrigerator then it is not serving the countertop even if located above the countertop.
Neither does the exception say that it IS an SABC, and context gives us no clarification. As I said at the outset, I have some evidence that supports my point of view, and I recogize that that evidence is not overwhelming. But I do believe there is even less evidence that supports your point of view. Let's just agree that neither of us can disprove the other's viewpoint. That work for you?By context, the exception permits an SABC for a refrigerator to be supplied by IBC (15A or greater). The exception does not say the circuit is non-SABC.
That is how I read the situation. It's probably the only place in the NEC that has such a strange set of requirements. :happyno:Again if I run an IBC to the refrigerator and install it on a 20 amp breaker then we must count it as one small appliance branch circuit and assign 1500 va, however if I run a 15 amp IBC to the same refrigerator I don't need to assign it 1500 va???
That wasn?t David?s point. He was suggesting that the countertop receptacle that happens to be a simplex and that happens to have a fridge plugged into it could count as one of the two required SABCs, so that only one more would be needed. I am inclined to agree, though I suspect most of us would consider that a poor design.
We don?t have to know or care what the homeowner chooses to plug into any given receptacle. If it is above the countertop, and if it is on a 20 amp circuit (individual or otherwise) then it is a SABC.
There is no such load calculation considered if designed as an individual branch circuit supplying a single refrigerator. When designing an individual circuit the load is limited to a specific appliance. However the circuit is not extending to other receptacle unless it is no longer considered an individual circuit and considered a small appliance branch circuit
The refrigerator installed with a 20 amp IBC is, IMO still part of the small appliance branch circuit just as it is stated in 220.52.
This is when we have a 15 amp cir. I don't see where it excludes the 20 amp cir
David it sounds like you are just saying your opinion. The refrigerator installed with a 20 amp IBC is, IMO still part of the small appliance branch circuit just as it is stated in 220.52. The fact That I choose to make it an individual circuit or not does not or should not change what it is called.
In terms of the 15 amp IBC for a Refrigerator-- IDK-- it seems that if the 20 amp is considered a small appliance branch circuit for the frig. then the 15 amp cir ought to be also but there is a large difference in calculating it at 1500va vs perhaps 600 or 700 va.
If I am to calculate any small appliance branch circuit over the req. two at 1500va and 220.52 tells us the refrigerator is part of the sabc then if I i9nstall it on an IBC it should be calculated at 1500va.
When I said "by context" I was including the exception to 220.52...Neither does the exception say that it IS an SABC, and context gives us no clarification.
..where it infers it is an SABC.Neither does the exception say that it IS an SABC, and context gives us no clarification.
I concur the [your :roll:] evidence is not overwhelming... and I believe there's more to support my conclusion.As I said at the outset, I have some evidence that supports my point of view, and I recogize that that evidence is not overwhelming. But I do believe there is even less evidence that supports your point of view. Let's just agree that neither of us can disprove the other's viewpoint. That work for you?