growler
- Atlanta,GA
BTW: How many arc fault receptacles or circuits have you installed for replacements?
They can water-board me all they want and I'll never tell.
Have you seen any that other contractors have installed?:?
Absolutely correct.
I agree with the others that the GFCI protection of the replacement, where specified in the current Code that applies in your customer's jurisdiction, is required, and there is no way to avoid it.
However, AFCI is another matter. If you pigtail the new replacement receptacles onto the existing wiring with just a little bit of new conductor, this pigtail allows you to invoke 210.12(B) Exception and waive the AFCI. This works under the 2014 NEC only, and is so solid (though heretical to some of the safety minded) that the removal of it applying to 406.4(D) Replacements is having to be added to the 2017 NEC.
Yes, Al is trying to invoke 210.12(B) exception by adding a short piece of wire. What he is saying is if you don't install the extra conductor (pigtail) then 210.12(B) ex. cannot be used-- but pit a 6" pigtail and you can use 210.12(B) ex. This is an attempt to work around a code article that IMO, is clear. It would make no sense to approve one install and not the other. The intent is to install afci when you change the receptacle if it is in an area where afci's are requiredyou are sayiing if i install a pig tail at each receptacle. i dont have to install AFCI per NEC2014. IYO.
Yes. In my opinion, the 2014 NEC AFCI requirement for replacement receptacles does not occur in 406.4(D) and one is told in 406.4(D) to follow the rule "elsewhere in this Code." This invokes 210.12 in its entirety, including the 210.12(B) passage on modification, which is in turn specifically given the Exception.you are sayiing if i install a pig tail at each receptacle. i dont have to install AFCI per NEC2014. IYO.
While you claim to "know" this Dennis, the differentiating between panels and devices is simply not to be found. In fact the IAEI in The Analysis of Changes in the 2014 NEC themselves did not make the distinction.I don't see it as Al does. IMO, these are two separate animals. Although I understand where he is coming from IMO those who believe this are stretching the codes intent for this. The main intent of 210.12(B) exception was for panel changes. Replacing a receptacle falls in a different category.
The 210.12(B) Exception is so solidly linked to 406.4(D) that NEW text is being added (it looks like) to the 2017 NEC to say that the exception can't be used with replacement receptacles.
It doesn't matter what you claim the "intent" is if the language actually says something other than your intent. The language is the "law", not your "intent".
I wrote the section and the 6' was added to basically what I wrote. I am doing a bit more than assuming as I used the panel change out as my substantiationWhile you claim to "know" this Dennis, the differentiating between panels and devices is simply not to be found. In fact the IAEI in The Analysis of Changes in the 2014 NEC themselves did not make the distinction.
I do understand your sense of ownership of this, Dennis. But, even with your testimony to your intent in writing the proposal, that doesn't change the fact that "intent" is not Code.I wrote the section and the 6' was added to basically what I wrote. I am doing a bit more than assuming as I used the panel change out as my substantiation
Where's the answer to the question already asked: why require AFCI for a receptacle change when it isn't required for a panel change?:?.
That's just it, isn't it. This question's answer is, in my opinion, still evolving. I can't wait until the 2017 NEC text is finally bedded. At this point it seems that there will be some new exceptions to add to how to answer your question.
I do not feel ownership as it technically isn't my proposal in toto but often times we have used the substantiation to understand the intent. I have not look that up because I am lazy but I assumed it was similar to what I stated.
Also I agree intent is not in the code I just don't agree with your interpretation as I see the 2 sections as different animals regardless of intent
Well, the Code Making Panel sure disagrees with you, as they seem to be adding to the 2017 NEC that the 210.12(B) Exception CAN'T be used with 406.4(D). . . which means that, in the CMP's mind, the 2014 NEC 210.12(B) Exception CAN be used with 406.4(D).
Ok. So, here: This is your proposal. CMP2 says, unambiguously, that YOUR intent is satisfied. That is to say, given all your certainty that it is an "incorrect interpretation" to apply 210.12(B) Exception to replacement of receptacle devices, here, below, in YOUR proposal, M. Hilbert clearly states that 210.12(B) Exception does, in fact, apply to the replacement of devices.Or it can mean that since many are interpreting this incorrectly and clarification is needed.![]()
2-115 Log #536 NEC-P02 Final Action: Accept in Principle
(210.12(B))
Submitter:
Dennis Alwon, Alwon Electric Inc.
Recommendation:
Add new text to read as follows:
Exception: Where extension of the branch circuit does not include any added outlets or devices.
Substantiation:
Often times when changing a service in an older home the branch circuit conductors do not reach the new location of the panel. The wire is sometimes just spliced inside the panel to reach the termination points while other times the circuit may need to be extended a short distance to reach the new location. Since many areas are inspecting this differently throughout the country this exception would clarify this section and bring uniformity throughout.
Panel Meeting Action: Accept in Principle
Revise the proposed wording to read as follows: "Exception: AFCI protection shall not be required where the extension of the existing conductors is not more than 1.8 m (6 ft.) and does not include any additional outlets or devices."
Panel Statement:
The revised wording provides clarity and satisfies the intent of the submitter.
Number Eligible to Vote: 11
Ballot Results:
Affirmative: 9 Negative: 1 Abstain: 1
Explanation of Negative:
KING, D.: This Proposal should be rejected. It is the intent of Section 210.12(B) to provide AFCI protection where circuits that are covered by 210.12(A) are "modified." The submitter has not provided any substantiation to allow for an exception for AFCI Protection in the branch circuit modification described in his substantiation. Accepting the proposed exception would greatly dimish the level of safety currently provided by the requirements of 210.12(B).
Explanation of Abstention:
ORLOWSKI, S.: See my Explanation of Vote on Proposal 2-92.
Comment on Affirmative:
HILBERT, M.: Continue to accept in principle. The issues noted in the substantiation for this proposal and Proposal 2-11 are often topics of discussion at IAEI meetings as well as other educational meetings and do need clarification.
The proposed language as revised by the panel's accept in principle action will go a long way in promoting uniform interpretations. It will clarify that extending branch circuit conductors within an enclosure for the purposes of replacing a device or utilization equipment or for extending a branch circuit to a panelboard being replaced or upgraded does not require an AFCI protective device to be installed.
Six feet was chosen for branch circuit extensions as it should provide a sufficient length for most applications where an existing panel is being relocated out of a clothes closet or to comply with readily accessible requirements, etc