Oh and how does this really clarify things?
210.12(B says to install afci where circuit is modified,
So then what is the purpose of 406.4(D)?
406.4(D) is specifically targeted at a replacement receptacle is it not?
As per your argument Al, you refer to the exception in 210.12. (extensions less than 6') and then say you do not need to add AFCI.
So I ask once again when would 406.4(D) apply if ever in your mind.
If never why is the code there?
There must have been a reason?
There must have been intent!
I could care less , however i'd like to make my installations code compliant and not have any backlash for doing so.