Strathead
- Ocala, Florida, USA
- Electrician/Estimator/Project Manager/Superintendent
Here is a mind twister to me. I was floored the other day, when I was discussing and (I now believe mistakenly) was lead to believe that the code doesn't limit the number of light fixtures on a branch circuit in a dwelling unit. Correct me if I am wrong, but right here, people have contended that there is no limit to the number of receptacles on a branch circuit in a dwelling unit? I was hung up on this for a couple days, but have come to this conclusion:
220.18 states that the total load shall not exceed the rating of a the branch circuit. Even though the code calculations for 220.12 show the minimum number of branch circuits that can feed a dwelling unit, they don't supersede 220.18 so there has to be a determination of the impact of each outlet on any one branch circuit. You can't count a duplex as zero amps just because nothing is plugged in to it at the time. So I contend that the 90va per single receptacle of 180va per duplex is required by code, just like 150va per 2 feet of track and the maximum lamp wattage of a fixture and all of the other load guidelines in article 220.
So my questions: Am I remembering correctly that it has been contended here that you don't have to limit the number of duplexes on say a 20 amp dwelling unit branch circuit. If so, those that feel that way. what is your position on what I wrote above.
After reading this a couple times I contend that you do, in fact, have to limit the number of duplexes on a branch circuit to the factor of 180va per. And if you don't, do you believe you can put an unlimited number of can lights on a dwelling unit circuit as well?