So now we need to put a line reactor ahead of the service or move the house further back on the property? Sounds reasonable.
And/or ask the poco for a higher impedance Xformer
~RJ~
So now we need to put a line reactor ahead of the service or move the house further back on the property? Sounds reasonable.
The AFCI does not have a lower magnetic (instantaneous) trip than a standard breaker. The 75 amps for the AFCI is the amount of current that must be flowing in the circuit before it looks for a parallel arcing fault.4. Everything is perfectly complaint, but because it's proximal to the serving Xformer, the refer motor exceeds the afci 75A mag trip.
~RJ~
The AFCI does not have a lower magnetic (instantaneous) trip than a standard breaker. The 75 amps for the AFCI is the amount of current that must be flowing in the circuit before it looks for a parallel arcing fault.
The electronics have nothing to do with the trip curve. The electronics act to open the circuit when they think it should be opened.I partly disagree. In the trip curves Steve posted the magnetic trip threshold begins at around 7x (105 amps), where are older none AFCI breakers were 10x and higher. Electronics then bring the trip curve down to 75amps when "arcing" is detected. In a sense an AFCI is a low mag trip breaker with signature analysis beginning only where nuisance tripping would begin from lowering the regular magnetic trip.
As I understand it, the AFCI looks for series arcs only when the current exceeds 5 amps and looks for parallel arcs only when the current exceeds 75 amps.So in theory if the current is not above either the series or parallel arc detection threshold there can be no nuisance trips from signature analysis alone.
Vacuums and refrigerators need to pull at least 7 or 8 amps to cause a trip unless there are other loads on the same circuit?
The electronics have nothing to do with the trip curve. The electronics act to open the circuit when they think it should be opened.
So in theory if the current is not above either the series or parallel arc detection threshold there can be no nuisance trips from signature analysis alone.
Vacuums and refrigerators need to pull at least 7 or 8 amps to cause a trip unless there are other loads on the same circuit?
So, the UL 1699 standard for AFCIs has roughly (50) different performance tests. Once you strip away the "standard" tests done on ALL electrical devices that ensure the product is safe from shock, fire, damage, etc.; what you are left with are primarily performance tests to prevent unwanted tripping.
For instance you have:
> Overvoltage, Undervoltage, Voltage Variations & Surge Voltage Tests (Ring Wave & Combination Wave)
> Loading Condition Tests (Inrush Current, Normal Operating Arcing, Non-Sinusoidal Waveform, Cross-Talk, Multiple Load, Lamp Burnout)
> Operation Inhibition Tests (Signal Masking, EMI Filter, Line Impedance)
> Resistance to Environmental Noise Tests (Electrostatic Discharge, Electromagnetic Field, Electrical Fast Transient, Induced RF Fields)
And there are a few others.
Those conditions can not reflect every single waveform that might be encountered in the real world. Its just a very small sample.
In order for a household refrigerator or freezer to be listed to the UL 250 standard, they must also go through a series of performance tests to ensure they do not operate outside any of the parameters set within that standard while under a host of varying conditions. None of those parameters are permitted to exceed the thresholds of the unwanted tripping tests in the UL 1699 standard for AFCIs.
Yet, in the real world we still see tripping. Probably because UL doesn't test each and every fridge with each and every AFCIs under each and ever condition.
A refrigerator is nothing more that a few motor loads, lighting loads, and perhaps a few electronic loads. None of the operational characteristics of these types of loads are subject to unwanted tripping IF they perform to standard.
That is incorrect. An inverter driven compressor is far from a few electronic loads. It produces a distinct waveform that could be mistaken as arcing.
One of three issues must be occurring in order for an AFCI to trip on a branch circuit supplying an outlet connected to a refrigerator:
1. The AFCI is damaged or defective.
2. The refrigerator is damaged or defective. (Any one part or component)
3. The wiring &/or terminations are defective.
Or the AFCI makers are not aware of a new waveform signature they must take into consideration.
That's it. The rest is simple algebra.
If only those doing wave signature analysis engineering were relying on simple algebra :lol:
If the AFCI and refrigerator are to standard, the wiring is the culprit. If the AFCI and wiring are to standard, the refrigerator is the culprit. If the refrigerator and wiring are to standard, the AFCI is the culprit.
So you admit AFCIs can be a culprit?
Anything lacking clarity is debateable Mr MBrooke.
Further, anything we as electricians install should be readily diagnosable , the manufacturer should be liable for their performance , specifications, statistical analysis , lab testings, marketing claims, etc.
Short of this , we will simply assume more threads like these, along with the blame being foisted on the consumer or installer.
This is why i would encourage anyone out there eating service calls over these devices to investigate them
Good day to all
~RJ~
Anything lacking clarity is debateable Mr MBrooke.
Further, anything we as electricians install should be readily diagnosable , the manufacturer should be liable for their performance , specifications, statistical analysis , lab testings, marketing claims, etc.
Short of this , we will simply assume more threads like these, along with the blame being foisted on the consumer or installer.
This is why i would encourage anyone out there eating service calls over these devices to investigate them
Good day to all
~RJ~
The electronics activate a solenoid that moves the same trip lever that the thermal and magnetic trips do. If there is no trip command from the electronics, the breaker acts as a standard thermal magnetic breaker. The same thing happens when the electronics fail...you just have a standard thermal magnetic breaker.Then how does the breaker trip? :blink:
The concept of the AFCI has nothing to do with instantaneous (magnitic)tripping based on the current....it only has to do with the detection of an "arc signature" (what ever that may be, and it is different for each manufacturer). The 75 amps was selected for the electronics to start looking for an arc signature, to reduce false trips. If they set it below the 75 amps there would be even more false trips than we have now.The electronics have their own response to conditions. In the case of parallel arc faults that condition begins at 75 amps. At 75 amps the electronics look for a current signature indicative of arcing. The electronics are intentionally doing what magnetic tripping can not do because a magnetic trip of 75 amps will nuisance trip some motors. Thus manufactures decided to set the magnetic trip on AFCI starting at 7x which takes care of parallel arcs exceeding over 100amps. However the blind spot between 150 amps and 75 amps is covered by the electronics.
The only reason there is electronics is because you need a "smart" device to detect "arc signatures". A standard thermal magnetic breaker can only react to current, not not to "arc signatures".Thats the only reason why electronics are involved in branch feeder AFCIs to begin with.
No. They were added to create the AFCI. You can't have an AFCI without electronics. A standard breaker cannot detect "arc signatures".Electronics were added to AFCIs to ironically stop nuisance tripping. ....
No. They were added to create the AFCI. You can't have an AFCI without electronics. A standard breaker cannot detect "arc signatures".
The electronics activate a solenoid that moves the same trip lever that the thermal and magnetic trips do. If there is no trip command from the electronics, the breaker acts as a standard thermal magnetic breaker. The same thing happens when the electronics fail...you just have a standard thermal magnetic breaker.
The concept of the AFCI has nothing to do with instantaneous (magnitic)tripping based on the current....it only has to do with the detection of an "arc signature" (what ever that may be, and it is different for each manufacturer). The 75 amps was selected for the electronics to start looking for an arc signature, to reduce false trips. If they set it below the 75 amps there would be even more false trips than we have now.
The current could be hundreds or even thousands of amps, but if there is no "arc signature" the electronics will do nothing. The circuit will be opened by the thermal and/or magnetic trip devices based on their curves.
If the current is below the 75 amps, the electronics do nothing but use a small amount of power.
The only reason there is electronics is because you need a "smart" device to detect "arc signatures". A standard thermal magnetic breaker can only react to current, not not to "arc signatures".
I disagree. A breaker with a low enough magnetic trip will mitigate parallel arc faults.