HELP!!!!! === BLACK FLUORESCENT TUBES- BALLASTS
fse
Minnesota
I recently installed 60 of these 2 lamp fluorescent fixtures, each with black tubes. Also installed 20 of the same fixtures with standard white T8 tubes. Since the new install, 4 months ago, we have replaced almost all of the black tubes and 25 ballasts in those black light fixtures (standard 2 lamp open strip fixture).
None of the white tube fixtures have been affected.
now a month after replacing them, at least another 70 bulbs and 12 ballasts are out again on the black tube fixtures only.
It is in a laser tag area and a new ARCADE area with 50 new arcade games. Power for the lights and games are on the same newly installed panel. The same panel has a new roof top fed from it also.
Can anyone help me out on this as to why the black tube fixtures are going so quickly!
Power company has had no power surges either. and the main power usage for the building is not an issue either.
Thanks
Ryan
I am not that familiar with those lamps but I would likely start by looking up the manufacturers stated lifespan and compare it to the standard lamps.
these lamps are rated for 20,000 hours! And they do not run all day, only when the laser tag area is used - so maybe 5 hours a day......
Some ballasts are rated only for use with power saving 36W 48" tubes while the black light tubes are almost certainly normal 40 watt design.
I would suspect a bulb/ ballast/ voltage mismatch somewhere.
Are the black light bulbs Rapid Start or thermal starter? And are the tombstones wired correctly?
I'm guessing golddigger is correct.
Check the blacklight bulbs are they F32 T8, F40 T8 or are they T12's? I found T12 4' blacklight bulbs to be easier to find.
Then open the fixture and check to see if ballast lists the bulb you are using.
Assuming that the OP installed T8 blacklight bulbs and the ballasts are spec'd for T8s, could it just be poor quality bulbs? I'm not familiar with any of the usual manufacturers making a F32T8-BLB.
The ballast are F32T8, instant start.
The black light bulbs are 32 watt, style BLB for black light bulb
no they are different suppliers / brands
Who's lamps and ballasts? part numbers?
Is the ballast manufacturer and lamp manufacturer paying you for material and labor to reinstall?
Sylvania does, but I don't see them making an F32T8/BLB
Universal and Advance ballasts also have a decent warranty program, they don't pay your full labor rate, but it's better than doing it for free.
Still available in 6 pack! :thumbsup:
I would say the thing to do is buy GE ballasts and lamps.
GE ballasts: http://www.gelighting.com/LightingWeb/na/images/16233_UltraMax_T8_Brochure_tcm201-20993.pdf
We have been using the MAX-N-Ultra ballasts for a few years and I don't recall ever replacing any under warranty.
I would contact a GE rep and see how their warranty program works if you use their lamps + ballasts.
Sylvania extends their warranty when you use all Sylvania in fixtures, not sure how GE works.
The ballast manufacturer is Cooper and the bulbs are some generic garbage - we don't know where they came from - my supplier says Candela.....but they are not what we specified, HIKARI lamps are the ones we wanted.
Cooper is paying for replacement of the ballasts for the first round of replacements but not sure on if they will this time around.....
Thanks for the info - I will check this out. Not sure what to do though with this if COOPER wants to replace with their own ballasts!
If you didn't get what you specified you should either get money back or the vendor needs to give you what you spec'd.
