delfadelfa
Member
- Location
 - Cincinnati, OH
 
I had a customer call about and arc-fault tripping when his treadmill is running.  This is a two year old condo.  He did not have a problem until he bought a new treadmill and plugged  it in a finished basement receptacle.  It does not trip the treadmill circuit but two other arc-fault breakers.  I pulled both breakers and made sure they were wired with the correct neutrals.   I added a 20 amp dedicated circuit by the panel for the treadmill and started the treadmill, within a minute both breakers tripped.  I checked the phases to see if the tripped breakers were on the same phase as my new circuit.  Only one arc-fault was on the same phase as the new circuit with the treadmill.  I switched both arc-fault breakers, this made no difference, the new arc-fault breakers tripped only when the treadmill was running just like the other ones.  The treadmill is rated for a total of 11 amps,  it never pulled more than 7 amps.  The two tripping arc-fault breakers will not trip when the treadmill is not running.  Has anybody run into anything like this where a circuit not connected to anything else in the house is tripping two other circuits??
	
		
			
		
		
	
				
			
				