ggunn
- Austin, TX, USA
- Electrical Engineer - Photovoltaic Systems
It is easier to mash potatoes than to pee green soup.I did.:?
What's wrong with spade lugs? In the nuclear industry, we were never allowed to use stranded wire without lugs. Safety and reliability is a BIG deal! Takes little time and works great. All I use when terminating strands under a screw. All my experience is utility or industrial, though.
Thought you had a dyslexia moment, but see otherwise now.Did ya' miss the pun?
By adding spade lugs you have doubled the number of terminations. More terminations results in more points of potential failure.
It just that they introduce one more point of possible failure.
What is going on??? Is Rodney Dangerfield in town?
I did a project for the Corps of Engineers on a dam. They insisted on RING terminals! Talk about a PITA...I assume you mean fork terminals. It just that they introduce one more point of possible failure. Many gov specs call for them, but I do not see them as better than a standard termination, perhaps cleaner depending on the person doing the work.
No sense of adventure.I use backwired devices with stranded wire.
Why not use a back wired pressure plate receptacle? Easiest solution if you struggle with stranded wire.
That's fine until the insulation comes off and leaves a 1/2 inch or so of bare conductor sticking out.
Some electrical/electronic components come with leads already stripped that way.+1. THIS is what I stock on my truck. I prefer not to terminate stranded wire on screw terminals and most the time I do not have to. These are great because they come with one of the screws already tightened. One just strips the wire, insert into back and tighten. A real time saver.
One only needs to leave a very small amount of insulation on the end of the wire. About an 1/8th inch will work just fine. This works very well IMO. I typically use my Klein Katapult strippers and with practice it is quite easy to strip the wire and leave the insulation just barely on the end of the wire. It is terminated and then the insulation is pulled off for a clean and precise job.
Don't the also have some glue on the end to keep the insulation from falling off?
IMO leave a lot—1/2" plus—then either leave it on (tape it back to itself if you are leery of the insulation coming off) or cut wire off flush with rear of device after tightening the screw....
I never noticed any.Don't the also have some glue on the end to keep the insulation from falling off?
I try to avoid using stranded wires on screw terminals. When I do it I like to leave a small section of the stripped insulation on the end of the wire. This keeps the strands from coming apart.
Ouch!!!It is easier to mash potatoes than to pee green soup.
By definition stranded wire is a flexible connection. Does the code not require flexible connections to be terminated with a terminal ( sta-kon) connection on a screw unless the screw is rated for this( i.e. a breaker terminal screw)
