chris kennedy
- Miami Fla.
- 60 yr old tool twisting electrician
What exactly is a "Site-Isolation Device"?
The 547.2 def is unclear to me.
Thanks
Thanks
I don't believe you can. 547.9(A) requires...I saw that Bob, but isolation leads me to believe I may also have to open the grounded conductor???
Even if you disconnect the load-side grounded circuit conductor, all the grounding is still connected to the line-side grounded circuit conductor.(4) Bonding Provisions. The site-isolating device enclosure
shall be connected to the grounded circuit conductor
and the grounding electrode system.