547
I saw that Bob, but isolation leads me to believe I may also have to open the grounded conductor???
I don't believe you can. 547.9(A) requires...
(4) Bonding Provisions. The site-isolating device enclosure
shall be connected to the grounded circuit conductor
and the grounding electrode system.
Even if you disconnect the load-side grounded circuit conductor, all the grounding is still connected to the line-side grounded circuit conductor.