We have a pretty big solar ground mount comming, We are installing a new 1600 amp 480 volt solar loads only service ,with new transformer from poco, no rule 16 yet from paco (rule 16 distribution line extensions) Plans call for 5 3" conduit using 300 mcm copper for each conductor run in parallel from Xfmr to switchgear . 300 mcm ampicity is 285 at 75c, 5 times 285 =1485. I'm guessing 1485 amps is the max that the photovoltaic system will produce shouldn't we be basing it on the 1600 main OCPD, I'm I missing something, I'm thinking 300 mcm is to small