I was told by my AHJ that TR is required in dorms as replacements as well as new construction.
Article 406.12 does not list dormitory units.
There has been some confusion between "Guest Rooms and Guest Suites of Hotel and Motels" and "Dormitory Units".
For comparison ARC fault article specifically lists Dormitory units in 210.12 (C).
Also 210.60 lists "Guest Rooms, Guest Suites, Dormitories and Similar Occupancies" as a group, for placement/location of receptacles.
So why are "Dormitory Units" not listed in 406.12 if the intention is to have TR in dorms?
Article 406.12 does not list dormitory units.