You can use the existing 3 wire outlet and change the cord on the dryer to match. I don't have the code section handy.
One way your modifying a factory cord, the other way your falsely connecting a 4 wire receptacle.
To me, both seem odd.
JAP>
Or also leave the factory 4 wire cord on the dryer, change the receptacle out to a 4 wire, and, jumper the grounded and EGC I take it?
The factory cord on the dryer s not your standard eyelet type connection. It is male to female quick connectors.
JAP>
I have never seen a dryer or range come from the factory with a cord....
Nor me until today.
This dryer came with a factory 4 wire cord where the White and Red wire were paired in the same 2 pole female connector, Black in it's own connector and Green with an eyelet on the end of it.
JAP>
Nor me until today.
JAP>
Do you know the manufacture/model? Just curious since like others i have not run into that yet. Maybe they offer a different cord or an adapter.
If #12 EGC from laundry duplex is too small for NEMA 10-30R electric dryer branch circuit, can laundry plumbing be a grounding extension per NEC 250.130(C)?
250.140 Exception: For existing branch-circuit installations only where an
equipment grounding conductor is not present in the outlet or junction
box, the frames of electric ranges, wall-mounted ovens, counter-mounted
cooking units, clothes dryers, and outlet or junction boxes that are part
of the circuit for these appliances shall be permitted to be connected to
the grounded circuit conductor if all the following conditions are met.
(1) The supply circuit is 120/240-volt, single-phase, 3-wire; or
208Y/120-volt derived from a 3-phase, 4-wire, wye-connected
system.
(2) The grounded conductor is not smaller than 10 AWG copper or
8 AWG aluminum.
(3) The grounded conductor is insulated, or the grounded conductor
is uninsulated and part of a Type SE service-entrance cable and
the branch circuit originates at the service equipment.
(4) Grounding contacts of receptacles furnished as part of the equipment
are bonded to the equipment.