Sure you can and Russ is incorrect. A panelboard or load center cabinet is simply that and used with a proper cover it becomes a Jbox. I would like for Russ to give us an example of a real written instruction that would apply.For a decommissioned panelboard and if the guts are removed, can you use this cabinet as a pullbox? Came across an article in EC&M and Russ LeBlanc says it violates 110.3(B) but I've seen this done before.
I agree with Roger. You are not using the enclosure as something other than an enclosure. I usually seal them with a screw on the side to prevent easy access.
Roger
I would like for Russ to find another job. This is not the first time he has put a blatant mistake into print in that major electrical publication.
[h=5]Cabinet.[/h]
An enclosure that is designed for either surface mounting or flush mounting and is provided with a frame, mat, or trim in which a swinging door or doors are or can be hung.
Either way assuming the wire nut is the correct size. I have installed ground bars in many junction boxesShould they all be wire-nutted together or would it be Code compliant to land them all on the existing ground bar in the cabinet ?