strugglinsparky
- Fort Collins, CO
Hi everyone. Usually just use this awesome site as a reference, but I couldn't find a post that delt with this.
A local heating company called me out to a house that the A/C inrush would cause all the lights to flicker and all the electronic clocks to reset. Lights flicker on inrush I have witnessed many times and I do not believe there is a fix or a issue with this, but every electronic clock in the house resets!!??. Microwave, electric range, sprinkler clock, digital garage door opener, everything resets to 12:00. They do not have any simple clocks House is out in the country and the only house on the local transformer, at the end of the POCO overhead line. The homeoners said this all started after they had a A/C installed. We did not wire the A/C so I was really hoping to blame the electrician.
Voltages all were "normal" at around 120v. There was only a max of 1v difference between A/B at any time. The lowest I witnessed was 118.5v at the house panel, when the A/C started up. The amperage on the house was 6 on A and about 15 on B. The voltage did increase a bit to the exterior disconnect (80' 4/0 SER) and a bit again to the pole disconnect (200' 250 MCM URD). 120/240 200 amp service. I use just a basic klein multi meter, so really quick fluctuations I cannot see. I checked for any hot connections with a temp gun and tested for torque. The highest inrush I measured was 22 amps and the running amps of the A/C was around 7.2. Nameplate on A/C was 18.2 min circuit with a 30 amp max overcurrent. I did not see the FLA/LRA. I was expecting much higher readings on the A/C. I texted the heating company tech but have not heard back yet.
I am perplexed.
I am perplexed.