This might be an example of that. This is a Seattle City Light transformer. I dont know what their "official" distribution voltage is, but it is often called 25.5KV. You can see the transformer doesnt say that.
The transformer does say that.
25570/14750
120/240
that means the transformer is for a 25 kV system, and outputs whatever the input is Divided by 61.45
so for that one, if the input is 14750V primary to gnd voltage, the output is 120/240 split phase
if it’s 14,400 in, then it’s 117/234 split phase.
it all has to do with thenXF TTR.
the TTR on transformers is wound with compensation for voltage regulation to standard nominals.
The POCOs run their voltages a little high through the regulators at the station or out on the line.
the “odd” readings you see are nothing more than fluctuations in the utility primary voltage.
on the transformer, rating is 25570 gndY/14750
that it 25570 primary L-L, and 14750 primary L-G
so, divide the 14750 by the 240, you get the XF TTR.
Take your voltage you read on your voltmeter (forget voltage drop on your wires in the house for now), multiply it by 61.45, or whatever your TTR calculates on your specific XF. That is the primary voltage at that moment.
We try to stay within a specific bandwidth.