mstrlucky74
- NJ
Picture just came in.Why would some if the feeder have 6 phase legs? So each set has 6 phase legs? Doesn’t make sense.
how about parallel 400 KCMIL for phase and neutral.
That would be 6 phase and two neutral wires.
maybe I’m missing something here..
what doesn’t make sense is parallel 400 (6 phase) with one neutral on the bottom section.
But parallel would be in different conduits.
Why?
i don’t see where it tells you how many conduits to run.
Theres a column for qty of sets.
I would have the same guess as Hv&Lv...2 parallel sets in each of 10 conduits would seem to be what it is suggesting to me. Do you have a riser?
If it shows one neutral that's one for each set correct?Not necessarily. You can put multiple sets in the same conduit, as long as you account for bundling adjustments, and the number of sets per conduit is uniform across the feeder. So 6 sets can be in 3 conduits with 2 sets in each, but 5 sets would have to each be in their own conduit. The drawings should specify whether multiple sets per conduit are intended.
Sent from my SM-N960U using Tapatalk
I follow what your saying but always thought parallel sets(wires) were always in separate conduits.
It's 20 conductors per phase in 10 conduits.
Plus 20 neutrals split between all the conduits?
Ive never worked on a service that large, so I’m curious.
my largest was a church with 6 conduits, one set in each.