Meter Socket Grounding
And if someone could educate me...lol....I assume the reason the meter loop would need bonded to the grounded conductor (neutral) is in case of a short which could result in a shock hazard?
Yes, a phase to the meter enclosure.
A few months prior to the area POCO mandating separate conduits, I found an up down loop that had one meter line side conductor shorted to the load conductor going back up that loop. We figured it out when the load side of the meter socket was still hot on one side after the meter was pulled. It could have been that way for years. Missed revenue for the POCO plus the safety aspect.
Yes, I meant grounding electrode system.
No, I think you are referring to having a fault return path. All metallic items on the line side of a service disconnect have to be bonded as per 250.92
The grounding electrode system is in addition to this.
Wow, interesting. Thanks for that knowledge. Isn't there a fuse that should have blown or something though?
You are correct, I got the GEC confused with the grounding conductor.
Let me ask this......if you installed a bronze grounding clamp on the aluminum conduit (the up/down meter loop) just below the weatherhead and put a bonding jumper from the clamp to the grounded conductor (neutral), would this be considered approved?
Do you own the meter loop or the POCO?
If you own it, do it over and bring the grounded conductor down in the meter loop. It does not need to go back up.
We can not have the line and load of that meter socket in the same raceway in this area. . The POCO does not supply up/down loops anymore. Only down, so a separate conduit back up for the load.
So how do you do your two separate conduits? One into the hub on top and how with the other conduit?
I think it is, but I'd have to look it up and I'm not able to do that right now.
Primary fuse on the transformer would have been the only fuse. IIRC the customer had old bare Cu overhead that had slapped together and given grief in previous years blowing the transformer fuse a time or two. The conductors got hot enough to melt the insulation.