And if someone could educate me...lol....I assume the reason the meter loop would need bonded to the grounded conductor (neutral) is in case of a short which could result in a shock hazard?
Yes, a phase to the meter enclosure.
A few months prior to the area POCO mandating separate conduits, I found an up down loop that had one meter line side conductor shorted to the load conductor going back up that loop. We figured it out when the load side of the meter socket was still hot on one side after the meter was pulled. It could have been that way for years. Missed revenue for the POCO plus the safety aspect.