- Windsor, CO NEC: 2023
- Hospital Master Electrician
You answered your own question: The load does not require a neutral.
On the line side, what you have labeled LV, there must be a neutral conductor from the source wye transformer neutral point to the neutral point of the three boost transformers.
A tightly coupled transformer reflects its secondary load impedance to its primary.
Making some guesses about context, where this might be used, transforming:If my load does not require a neutral, do I need to bring a neutral to the line side of this series of buck-boost transformers for proper operation?
I'm pretty sure you only need two. When you increase or decrease Vab and Vbc, Vca will take care of itself.More detail: this is using three buck-boost transformers, boosting 208V 3Ø to 240V 3Ø for a sensitive 3Ø load. There is no neutral required at the load.
I hadn't thought about a significantly reduced neutral just for the sake of voltage reference (no real current flow) - that sounds like the best approach.
Thanks!
I usually use the delta configuration, no neutral present or needed.If my load does not require a neutral, do I need to bring a neutral to the line side of this series of buck-boost transformers for proper operation?
We installed a 480/277V wye connected PV inverter through a transformer on a 208/120V service, but our installers improvised on the inverter placement and put it a lot farther away from the transformer (an autotransformer) than I designed the conductors for. The added voltage rise in combination with the fact that the POCO was operating in the top of its voltage range kept knocking the inverter off line. We consulted with a transformer company, who prescribed a pair of (as in two) buck/boost transformers to bring the voltage back into range at the inverter. It worked. It may very well be that the fact that it was an autotransformer made a difference, but I won't be using them anymore, anyway.200112-1241 EST
You people do not define what you are talking about.
George defined a circuit in the first post. I think his post was clear and defined. His question related to a question on whether or not he needed to run a neutral wire to the center point of his wye connected primaries of his three boost transformers. The answer is yes.
ggunn:
Your reply "I'm pretty sure you only need two. When you increase or decrease Vab and Vbc, Vca will take care of itself."
"Two" what? Remove one of his boost transformers, and now you have two boost transformer primaries connected in series across a source voltage. These transformers operate as impedance transformers, and the primary voltages divide the source voltage based on the reflected impedances which vary with load.
But you were really suggesting changing the circuit in more ways than just removing one boost transformer. This you did not state. Really you were suggesting that the boost transformers be reduced to two, and also changing from where the primaries were fed without stating the change in primary wiring. This new circuit will work. But makes the output line to earth voltages unequal. For a balanced load it makes the source currents unequal. All of this may be OK. We don't know,
A three phase inverter can typically deliver its designed output power equally into the three ungrounded conductors even if the grid-derived voltages are unequal. A grid interactive inverter cannot be characterized as a constant impedance load nor as a simple voltage or current source. Now the monitoring software of the inverter may trip out on too high a voltage imbalance between the wye to neutral voltages, which is a different problem.We installed a 480/277V wye connected PV inverter through a transformer on a 208/120V service, but our installers improvised on the inverter placement and put it a lot farther away from the transformer (an autotransformer) than I designed the conductors for. The added voltage rise in combination with the fact that the POCO was operating in the top of its voltage range kept knocking the inverter off line. We consulted with a transformer company, who prescribed a pair of (as in two) buck/boost transformers to bring the voltage back into range at the inverter. It worked. It may very well be that the fact that it was an autotransformer made a difference, but I won't be using them anymore, anyway.