- NE Nebraska
- EC
That is all fine and dandy, but who pays for all this, especially if you find nothing wrong? 99.99% of the time probably the contractorWhats the make and model of the microwave? Did i miss that?
To be sure its the AFCI and not the microwave or the wiring
I would fist disconnect all the end devices, the use an insulation tester, and run the same test done on manufactured homes and RV's (its in the NEC I believe).
That finds pinched wires, wet wires, screws and tight staples.
Then I replace the AFCI with a GFCI or even better a (Class B) 30ma GFCI breaker.
Here is one made by Siemens:
https://support.industry.siemens.com/cs/products/us2:qe115/brkr-qe2-gfci-30ma-1p-120v-15a-10ka?pid=899828&mlfb=US2:QE115&mfn=ps&lc=en-US
If your 'Class B' GFCI trips you actually have faulty microwave problem.
If the problem goes away try a adding a AFCI receptacle so just the microwave is AFCI protected.
Post the results back here.
I also have used a data logger to log the equipment ground, hot and neutral for a few days.
Add: even if the manufacturer/supplier decides to give you a replacement AFCI that has been updated and doesn't trip, you still put some time and other materials into this and will not be reimbursed.