electrofelon
- Cherry Valley NY, Seattle, WA
- Electrician
Our guys in the field sometimes send us pictures of crispy critters that have bridged the busbars in an MDP. Most often they are lizards.
Disappointed, opened this thread expecting to see an electrocuted fried hamster in a panel and left to wonder how the hamster got into the panel.
Right that is the question: if I can buy a MB load center and take the breaker from it. Probably cheaper than buying the breaker separately, as long as they haven't changed them. I never use Eaton so I'm not familiar with when they have changed things.Why not just buy the new breaker with the load center? The cost difference should be negligible. Plus that breaker has the appearance of being a bit beat.
Perhaps someone else can answer the question on whether that breaker can fit a new load center. But better way may be to get the serial number off of that breaker and contact your local Eaton rep comparing it to new load center if you insist on using that same breaker.
Thanks, do you know what the difference is between the CC and CCV?CCV2200
A little over $100
I think.it is just the cat number. You may have to remove the load lugs from the new breaker, I believe that is the way they come.Thanks, do you know what the difference is between the CC and CCV?
Another option is to buy a new panel and swap the new guts into the existing enclosure.
No, but I've done it plenty of times, especially in an emergency. I also use the new panel's front cover.Not going to be a direct swap, the load centers were redesigned since the panel in the OP's photo was built.
10k AIC will work just fine as long as your short circuit current isn't above 10k AIC.Only 10k AIC too, lame.
Well the local supply house had the CCV2200 which they said is the replacement for the CC2200. It fit perfect, just had to remove the load side lugs. Hated to do it, it was $200 but wasnt worth saving $80 buying online and going back another time. Only 10k AIC too, lame. Swapping the whole panel would have sucked. Thought about the gut swap, but didnt really want to deal with that either.
Is this right on the secondary of a small transformer? What size transformer and what is the voltage? We can guess the impedance of the transformer as 5.75% unless you know better.
If this 200A breaker and panel is fed from a distribution panel from a larger transformer, we can figure that out too. 10K AIC still might be good.
I bet I have 2 of those breakers in my basement that we pulled out of a job a few years back. I can check. If you want them I will send it to you. pm me... I will be home around 1pm